An S7 PLC should answer a ping. Did you put your PC (via a manual config) on the same local network as the roasters IP (thus on 192.168.100.x)? If you cannot ping the PLC from your computer it is unlikely that Artisan can connect to it. |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
Hello,
im trying to configure Artisan with Petroncini TT 5/10 (2020) equipped with the Avantgarde control system talking Siemens S7.
So before Configuring Artisan i would like get / check connectivity between devices.
Roaster operate on Windows CE where im not sure if threre is some update or drivers instalation needed.
So i would like to ask you about any help / tips what should i try and check.
Thank you very much for any respons.