Replies: 2 comments 4 replies
-
The Kaldi machine configuration is documented here on the Artisan website. It is for interfacing to a Kaldi with a MODBUS RTU connection. You mention using the Center 306 to measure temperatures on your Kaldi. That is a different configuration and requires setting the Meter to "Center 306" in Artisan's Config>> Device dialog. Be sure you choose the right Comm Port in the Ports Configuration. The Center requires a special cable to connect with your computer that should have come with the meter. Finally, the recommended driver is the Silicon Labs CP210x. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
I have a Kaldi Fortis roaster. I have installed the current version of Artisan (as of 01-01-25), installed the CH341ser.exe serial driver, configured Artisan for the Kaldi Fortis (supported roaster), tried each of the three com port settingn options (3,4 & 5) and still no luck having the temps come through to Artisan from the Center 306 Data Logger Thermometer. I appreciate any suggestions you may have.
Beta Was this translation helpful? Give feedback.